ICC - International Code Council
 
Cart                                                          
Skip to main content
 
Codes, Standards & Guidelines

Your ICC Account

Email:
Password:
Bookmark and Share
Certification Renewals

Codes & Standards Discussion Forum 

Welcome to the ICC Codes & Standards Discussion Forum

The Code Council has revisited how best to provide an online, professional Discussion Forum and area within the website that has a sense of community – where Members and nonmembers can provide input and exchange ideas with their peers in the industry. The new Codes & Standards Discussion Forum does just that, as it allows Registered Website Users and ICC Members to discuss the I-Codes in an online community.

Members Area Codes & Standards Discussion Forum

Note to Nonmembers: If you join the ICC you can have access to important building safety information!

Members Area Codes & Standards Discussion Forum

As an ICC Member, you have access to the Members Area of the Codes & Standards Discussion Forum. Follow the link to discuss the Membership Councils and other benefits of being an ICC Member.

Forums» Fire Codes» Fire Code 3705.4 - Ozone Gas Generator

2 post(s) First 1 Last
Search 
Fire Code 3705.4 - Ozone Gas Generator
This forum is under moderation. Your reply will appear when it is approved.
Fire Code 3705.4 - Ozone Gas Generator By  Nicole Persaud

Posts: 1

4/12/2012 3:39:07 PM

I am looking for clarification regarding where the Fire Code states:

"Piping, valves, fittings and related components used to convey ozone shall be in accordance with Sections 3705.4.1 through 3705.4.3.

 

    3705.4.1 Piping. Piping shall be welded stainless steel piping or tubing.

 

        Exceptions:

            1. Double-walled piping.

            2. Piping, valves, fittings and related components located in exhausted enclosures.

I have a 1.5 lb/day ozone generating system operating outdoors for the use of remediating groundwater contamination.  Telfon tubing and fitting are compatible with ozone and is being used as the conveyance material.  However, the local fire department is requirement the valves, fittings, and tubing to be within secondary containment.  Telfon alone should be acceptable. 

Is there any clarification regarding this section of the code for when a the ozone generating system is operating outdoors, i.e. already ventilated?

Thank you,

Nicole

Report Abuse     

   

Fire Code 3705.4 - Ozone Gas Generator By  Research Safety

Posts: 5

8/13/2012 2:36:04 PM

Standards are intended to provide reasonable safeguards. 

You could calculate how much air would be required to dilute an ozone tube leak to relatively safe levels (0.05ppm -0.2ppm per ACGIH).   This will give you an indication of the relative hazard of an ozone leak event and a relatively safe distance from a leak.  Additionally, the short half life and good physiological warning properties of ozone may be considered in a risk assessement.  Secondary gas piping only makes sense when the interstitial space is monitored for leaks and high exposure risk requires its use.

Report Abuse     

   