ICC - International Code Council
 
Cart                                                                   
Skip to main content
 
About ICC

Your ICC Account

Email:
Password:
Bookmark and Share
Cengage

Codes & Standards Discussion Forum 

Welcome to the ICC Codes & Standards Discussion Forum

The Code Council has revisited how best to provide an online, professional Discussion Forum and area within the website that has a sense of community – where Members and nonmembers can provide input and exchange ideas with their peers in the industry. The new Codes & Standards Discussion Forum does just that, as it allows Registered Website Users and ICC Members to discuss the I-Codes in an online community.

Members Area Codes & Standards Discussion Forum

Note to Nonmembers: If you join the ICC you can have access to important building safety information!

Members Area Codes & Standards Discussion Forum

As an ICC Member, you have access to the Members Area of the Codes & Standards Discussion Forum. Follow the link to discuss the Membership Councils and other benefits of being an ICC Member.


4 post(s) First 1 Last
Search 
R-value of flex duct
This forum is under moderation. Your reply will appear when it is approved.
Re: R-value of flex duct By  simon says

Posts: 0

1/21/2009 8:07:00 AM

Check in the applicable edition of the International Energy Conservation Code adopted by your jurisdiction. Refer to Section 403.2 "Ducts". Determine your area''s "climate zone" for any other insulation value requirements.


   

Re: R-value of flex duct By  jar546

Posts: 0

1/21/2009 9:07:00 AM

There is no R value required for ducts located within the building thermal envelope. I am assuming this is residential.

Outside the envelope required R-8

It does not matter what climate zone you are in.


   

Re: R-value of flex duct By  paul curry

Posts: 0

1/21/2009 9:10:00 AM

2006 IECC 403.2 Supply and return ducts shall be insulated to a minimum of R-8, in floor trusses, R-6.

EXCEPTION! Ducts within the building thermal envelope do NOT need to be insulated.

Now, you say the ducts are in the home''s envelope... are they in the THERMAL envelope? that means, within the insulated space, not in the uninsulated attic, etc.


   

Re: R-value of flex duct By  Jeff2121

Posts: 0

1/21/2009 9:54:00 AM

Thank you all, you guys have been very helpfull........Jeff


   