ICC - International Code Council
 
Cart                                                                   
Skip to main content
 
About ICC

Your ICC Account

Email:
Password:
Bookmark and Share
2015 I-Codes

Codes & Standards Discussion Forum 

Welcome to the ICC Codes & Standards Discussion Forum

The Code Council has revisited how best to provide an online, professional Discussion Forum and area within the website that has a sense of community – where Members and nonmembers can provide input and exchange ideas with their peers in the industry. The new Codes & Standards Discussion Forum does just that, as it allows Registered Website Users and ICC Members to discuss the I-Codes in an online community.

Members Area Codes & Standards Discussion Forum

Note to Nonmembers: If you join the ICC you can have access to important building safety information!

Members Area Codes & Standards Discussion Forum

As an ICC Member, you have access to the Members Area of the Codes & Standards Discussion Forum. Follow the link to discuss the Membership Councils and other benefits of being an ICC Member.


2 post(s) First 1 Last
Search 
Occupant load for mercantile space
This forum is under moderation. Your reply will appear when it is approved.
Occupant load for mercantile space By  KDS

Posts: 28

1/21/2012 1:25:31 PM

Say you have a retail space of 9000 s.f. on the grade floor. 9000 / 30 = 300 occupant load. Except that, once you add FFE, you're left with less than a third of that floor area that's occupiable. I don't think the intent of the code is to allow 300 people into a retail space with an occupiable area of maybe 3000 s.f., regardless of how many exits there are. Anyone care to comment? Thanks.

Report Abuse     

   

Occupant load for mercantile space By  Brian Little

Posts: 18

1/22/2012 2:26:19 PM

 Posted by Densel Kimbrough

Say you have a retail space of 9000 s.f. on the grade floor. 9000 / 30 = 300 occupant load. Except that, once you add FFE, you're left with less than a third of that floor area that's occupiable. I don't think the intent of the code is to allow 300 people into a retail space with an occupiable area of maybe 3000 s.f., regardless of how many exits there are. Anyone care to comment? Thanks.

30 gross for sales floor.  Includes FFE.  No stock room?  No restrooms?  No offices?.  

The intent is to provide a fairly conservative design occupant load for life safety issues.  I question the logic of tying plumbing fixture counts to egress occupant load.  But, what do I know?   