ICC - International Code Council
 
Cart                                                                   
Skip to main content
 
Membership

Your ICC Account

Email:
Password:
Bookmark and Share
Green Building Certification

Codes & Standards Discussion Forum 

Welcome to the ICC Codes & Standards Discussion Forum

The Code Council has revisited how best to provide an online, professional Discussion Forum and area within the website that has a sense of community – where Members and nonmembers can provide input and exchange ideas with their peers in the industry. The new Codes & Standards Discussion Forum does just that, as it allows Registered Website Users and ICC Members to discuss the I-Codes in an online community.

Members Area Codes & Standards Discussion Forum

Note to Nonmembers: If you join the ICC you can have access to important building safety information!

Members Area Codes & Standards Discussion Forum

As an ICC Member, you have access to the Members Area of the Codes & Standards Discussion Forum. Follow the link to discuss the Membership Councils and other benefits of being an ICC Member.


6 post(s) First 1 Last
Search 
When is a boiler room required?
This forum is under moderation. Your reply will appear when it is approved.
When is a boiler room required? By  Martzee

Posts: 3

8/21/2012 7:58:24 PM

Hello,

Can I get help on IBC 2009 table 508.2.5? It seems that 2009 version is no longer requiring 1-hour rated enclosure for boilers above 400,000 BTUH, since it calls only for furnace room and per IMC definition a furnace room is everything used for space or hydronic heating except boilers. The next line in the table speaks about boilers not being over 15 psi and 10 hp wouldn't need an enclosure.

 

Converting boiler 10 hp into BTU/h I get 25,444.33 BTUH. Does that mean, that literaly every boiler must be installed in a 1 hour rated mechanical room? Or how should this code be interpreted or applied?

 

Thanks for help

Martin

Report Abuse     

   

When is a boiler room required? By  mtlogcabin

Posts: 242

8/22/2012 6:25:35 PM

 Posted by Martzee

Hello,

Can I get help on IBC 2009 table 508.2.5? It seems that 2009 version is no longer requiring 1-hour rated enclosure for boilers above 400,000 BTUH, since it calls only for furnace room and per IMC definition a furnace room is everything used for space or hydronic heating except boilers. The next line in the table speaks about boilers not being over 15 psi and 10 hp wouldn't need an enclosure.

 

Converting boiler 10 hp into BTU/h I get 25,444.33 BTUH. Does that mean, that literaly every boiler must be installed in a 1 hour rated mechanical room? Or how should this code be interpreted or applied?

 

Thanks for help

Martin


Rooms with boilers where the largest piece of equipment is over 15 psi and 10 horsepower

The boiler has to meet both requirements before a 1-hour room or fire protection is required.

ICC does not stand for Intentionally Clear and Concise

Report Abuse     

   

When is a boiler room required? By  Martzee

Posts: 3

8/23/2012 11:11:27 AM

I am sorry, but I didn't ask for this. I know that. My question was:

 

Is the requirement of 400,000 BTUH no longer applied to boilers since IMC 2009 seems to be excluding it?

 

And second, how do you convert 10 hp? If you use regular conversion you get 25 MBH, is that correct and if so, does that mean that every boiler has to have an enclosure? A typical residential boiler is usually 30 psi and its capacity ranges from 50 - 400 MBH. so it would exceed (or meet) both requirements for enclosure. So I am suspicious about my conversion.

 

Thanks

Report Abuse     

   

When is a boiler room required? By  mtlogcabin

Posts: 242

8/24/2012 3:47:23 PM

 Posted by Martzee

I am sorry, but I didn't ask for this. I know that. My question was:

 

Is the requirement of 400,000 BTUH no longer applied to boilers since IMC 2009 seems to be excluding it?

 

And second, how do you convert 10 hp? If you use regular conversion you get 25 MBH, is that correct and if so, does that mean that every boiler has to have an enclosure? A typical residential boiler is usually 30 psi and its capacity ranges from 50 - 400 MBH. so it would exceed (or meet) both requirements for enclosure. So I am suspicious about my conversion.

 

Thanks

For fire protection requirements yes the 400,000 BTU's is no longer  the required number.

For a boiler room requiring 2 exits the 400,000 BTU's is still the number to use.

Although the IBC code does not clarify the 15 PSI requirement the definition  of  a low-prssure boiler does

 BOILER. A closed heating appliance intended to supply hot water or steam for space heating, processing or power purposes. Low-pressure boilers operate at pressures less than or equal to 15 pounds per square inch (psi) (103 kPa) for steam and 160 psi (1103 kPa) for water. High-pressure boilers operate at pressures exceeding those pressures.

Is it a steam boiler or a boiler for heating water.

I long for the more simple times when we did not need to ask for all the variables.

 

Boiler Horsepower - BHP

The Boiler Horsepower (BHP) is

  • the amount of energy required to produce 34.5 pounds of steam per hour at a pressure and temperature of 0 Psig and 212 oF, with feedwater at 0 Psig and 212 oF.

An BHP is equivalent to 33,475 BTU/Hr or 8430 Kcal/Hr and it should be noted that a boiler horsepower is 13.1547 times a normal horsepower.

  • 1 horsepower (boiler) = 33445.6 Btu (mean)/hr = 140671.6 calorie/min (thermo) = 140469.4 calorie (mean)/min = 140742.3 calorie (20oC)/min 9.8095x1010 erg/sec = 434107 foot-pound-force/min = 13.1548 horsepower (mech) = 13.1495 horsepower (electric) = 13.3372 horsepower (metric) = 13.1487 horsepower (water) = 9809.5 joule/sec = 9.8095 kilowatt

ICC does not stand for Intentionally Clear and Concise

Report Abuse     

   

When is a boiler room required? By  Ryan Wohlfarth

Posts: 1

9/12/2014 4:54:30 PM

Can anyone verify and give me a citation for this information?

I am trying to figure out myself when a 1 hour separation is required and it seems to me that it is only required when a boiler is above 10 HP AND 15PSI Steam/160 PSI water. 

 

THANKS!