ICC - International Code Council
 
Cart                                                                   
Skip to main content
 
Misc

Your ICC Account

Email:
Password:
Bookmark and Share
cdpACCESS

Codes & Standards Discussion Forum 

Welcome to the ICC Codes & Standards Discussion Forum

The Code Council has revisited how best to provide an online, professional Discussion Forum and area within the website that has a sense of community – where Members and nonmembers can provide input and exchange ideas with their peers in the industry. The new Codes & Standards Discussion Forum does just that, as it allows Registered Website Users and ICC Members to discuss the I-Codes in an online community.

Members Area Codes & Standards Discussion Forum

Note to Nonmembers: If you join the ICC you can have access to important building safety information!

Members Area Codes & Standards Discussion Forum

As an ICC Member, you have access to the Members Area of the Codes & Standards Discussion Forum. Follow the link to discuss the Membership Councils and other benefits of being an ICC Member.


3 post(s) First 1 Last
Search 
Foundation Rebar Clearance
This forum is under moderation. Your reply will appear when it is approved.
Re: Foundation Rebar Clearance By  Eagle

Posts: 0

5/26/2005 10:02:00 AM

Hey

For grade slabs and footings the IRC does not require reinforcement ... except for footings in SDC - "D" which must be 3" clear to earth per IRC R403.1.3

For reinforced foundation walls the required clearance for prescriptive reinforcement to earth is actually greater than 3" per the IRC R404.1 table footnotes.

If additional design steel is shown on the drawings, the clearances may also be shown ... subject to the 3" minimum earth clearance provision of ACI-318 as a reference standard per IRC Chapter 43

Might be good to add a general table on reinforcement clearances to the IRC for clarity ... ;-)

------------------
Rob
(2000 IBC/IRC)


   

Re: Foundation Rebar Clearance By  Paul Sweet

Posts: 0

5/26/2005 10:05:00 AM

IRC R403.1.3 requires bottom reinforcement in concrete footings located in Seismic Design Categories D1 and D2 to be located a minimum of 3 inches clear from the bottom of the footing.

I guess it doesn''t say anything about other footings, because it doesn''t require them to be reinforced.


   

Re: Foundation Rebar Clearance By  DaveW

Posts: 0

5/28/2005 5:43:00 AM

That''s it Eagle, ACI318. Thanks as that governs all placement of rebar a minimum 3 inch clearance from any soil no matter seismic zone. [IMG]http://www.iccsafe.org/ubb/biggrin.gif[/IMG]

[QUOTE]Originally posted by Eagle:
[b]Hey

For grade slabs and footings the IRC does not require reinforcement ... except for footings in SDC - "D" which must be 3" clear to earth per IRC R403.1.3

For reinforced foundation walls the required clearance for prescriptive reinforcement to earth is actually greater than 3" per the IRC R404.1 table footnotes.

If additional design steel is shown on the drawings, the clearances may also be shown ... subject to the 3" minimum earth clearance provision of ACI-318 as a reference standard per IRC Chapter 43

Might be good to add a general table on reinforcement clearances to the IRC for clarity ... ;-)

[/b][/QUOTE]



------------------
DaveW - Colorado - Have a Great Day -