The Code Council has revisited how best to provide an online, professional Discussion Forum and area within the website that has a sense of community – where Members and nonmembers can provide input and exchange ideas with their peers in the industry. The new Codes & Standards Discussion Forum does just that, as it allows Registered Website Users and ICC Members to discuss the I-Codes in an online community.

Members Area Codes & Standards Discussion Forum

Note to Nonmembers: If you join the ICC you can have access to important building safety information!

Members Area Codes & Standards Discussion Forum

As an ICC Member, you have access to the Members Area of the Codes & Standards Discussion Forum. Follow the link to discuss the Membership Councils and other benefits of being an ICC Member.

Forums» Plumbing, Mechanical and Fuel Gas Codes» Emergency shut off switch location for a gas furnace

5 post(s) First 1 Last
Search 
Emergency shut off switch location for a gas furnace
This forum is under moderation. Your reply will appear when it is approved.
Re: Emergency shut off switch location for a gas furnace By  Builder bob

Posts: 0

1/15/2009 4:52:00 AM

What type of equipment?
Read IMC section 1104.2 Machinery room
and IMC sections 1106.4 Flammable refrigerants. Where refrigerants of
Groups A2, A3, B2 and B3 are used, the machinery room shall
conform to the Class 1, Division 2, hazardous location classification
requirements of the ICC Electrical Code.
Exception: Ammonia machinery rooms.
[F] 1106.5 Remote controls. Remote control of the mechanical equipment and appliances located in the machinery room shall be provided as required by Section 606.9 of the International
Fire Code.

IFC section 606.9

606.9 Remote controls. Remote control of the mechanical
equipment and appliances located in the machinery room shall
be provided at an approved location immediately outside the
machinery room and adjacent to its principal entrance.
606.9.1 Refrigeration system. A clearly identified switch
of the break-glass type shall provide off-only control of
electrically energized equipment and appliances in the
machinery room, other than refrigerant leak detectors and
machinery room ventilation.
Exception: In machinery rooms where only nonflammable
refrigerants are used, electrical equipment and
appliances, other than compressors, are not required to
be provided with a cut-off switch.
606.9.2 Ventilation system. A clearly identified switch of
the break-glass type shall provide on-only control of the
machinery room ventilation fans.


   

Re: Emergency shut off switch location for a gas furnace By  Enessa

Posts: 0

1/15/2009 5:27:00 AM

Heating information: Nutone G7-60 split natural gas furnace with 90% AFUE.

Cooling information: Nutone FS4BD-30 13 SEER tonnage of 2.5.

The location is the ground floor of a townhouse unit in the unfinished recreation room. They have decided to finish it and build a closet around the mechanical equipment. The switch was going to remain in the same location but since the walls were put up, they were requested to move the switch to the outside of the closet.


   

Re: Emergency shut off switch location for a gas furnace By  Builder bob

Posts: 0

1/15/2009 6:59:00 AM

Is the switch being used as a means of disconnect?


   

Re: Emergency shut off switch location for a gas furnace By  Enessa

Posts: 0

1/15/2009 7:54:00 AM

Yes.


   

Re: Emergency shut off switch location for a gas furnace By  Builder bob

Posts: 0

1/15/2009 10:25:00 AM

Is this an issue from the electrical code about a locking means of disconnect or keeping the switch is open sight of the technician who has to work on the equipment? I am only guessing as I did not visit the site......Is the Code enforcement officer approachable for their reasoning?


   