Smoke Control Methods
November 27, 2012
4:59 pm
Avatar
briant@aegisengineering.com
Member
Guests

Members
Forum Posts: 80
Member Since:
June 29, 2015
sp_UserOfflineSmall Offline

Another approach applied in some facilities utilizes smoke barriers in accordance with 909.5 for smoke control.

On a recent jail project we utilized automatic roof vents for a performance-based smoke control design. This did rely on coordination/control/connection with the fire alarm system, but did not involve mechanical fan equipment.

November 21, 2012
9:57 am
Avatar
MRoempke@huntsvilletx.gov
New Member
Guests

Members
Forum Posts: 1
Member Since:
April 20, 2015
sp_UserOfflineSmall Offline

Using the 2009 IBC, I have an I-3 occupancy that is required to have an engineered smoke control sytem per section 408.9 and the smoke control system must be in accordance with section 909.  Section 909.6 appears to state that a "Pressurization Method" is the primary method to be used.  In an article of the ASHRAE Journal in July 2010 that speaks to HVAC and smoke control in jails, the article favors that engineered smoke systems should not be used in jails but a smoke purge system should be used.  Any thoughts with this complex issue?