2018 energy code r values
August 1, 2019
2:26 pm
Avatar
swilson@camdenmaine.gov
New Member
Guests

Members
Forum Posts: 1
Member Since:
February 4, 2019
sp_UserOfflineSmall Offline

R13 = 3.8 ci or R-20

The first number r-13 is the minimum r value of between the studs, using insulation such as fiberglass in a 2x4 wall, 3.8 ci is for R-3.8 continuous insulation (foam board, rock wool, etc) continuous on the exterior or interior of the framing. The total R of this configuration would be ~16.8 but due to the continuous 3.8 not being interrupted by framing the code considers this as compliant to R-21 as in a 2 x 6 wall with just batt insulation.

July 29, 2019
3:49 pm
Avatar
sefdesign@cox.net
New Member
Guests

Members
Forum Posts: 1
Member Since:
March 3, 2016
sp_UserOfflineSmall Offline

Energy code 2018 table C402.1.3.  climate zone 2, all other.  Wood framed and other.  Value reads ‘R-13 + R-3.8ci or R-20’  what is the final required value for wood frame with batt insulation and rigid insul board, R-16.8??  what is the R-20 indicate??