2 Story Duplexes w/Identical Floor Plans
July 19, 2017
7:05 am

Forum Posts: 3
Member Since:
April 7, 2015
Print Post Post #1

Based on the following code references: R302.3, R302.3.1, Table R302.1(2) and R310.1 of the 2012 IRC, I have rejected 3 duplexes. My reason being that it is infeasible for the design to comply with the code requirements since fire rated Floor/Ceiling assemblies are required to be supported by an equal or greater fire rated wall assembly, and bedrooms are required to have egress windows (openings). I would appreciate feedback agreeing or disagreeing with my rejection of these structures and my interpretation of the codes as applicable to these structures.